You must be having some industrial load or lots of offices with A/Cs etc. nearby and on the same transformer. They work in the daytime and due to their load the voltage is in limits. For these loads the EB must have raised to tap to keep stable voltage - you have to compensate the voltage drop. That is EB's mandate as per regulations.I still do have faults. Day time seems to be stable and voltage is around 230-240v and potential in neutral is within 6v. Night after 8 or 9 it’s very unstable.Good for nothing EB. Voltage is very high and at times 250-260v and there is a raise of potential in the neutral 6-17v.
These distribution transformers do not have automatic tap changers or what we call On Load Tap Changer. They have Off Load Tap Changer that is manual and can be operated only after switching off the load (not economical to have On Load TC - your tariff will be 4 times ). No one would come at night to change the taps to lower the voltage.
It is also normal everywhere the voltage surges in the night when the load drops. Again the neutral is set to rise at night as overall voltage profile rises and there is more current due to unbalanced nature of loads.
You need a dedicated transformer if these have to be solved