Hi,
I have paired this model APC BR600 (360W ) costing 2.5k to my optoma HD20.
But when the power goes off, PJ also went suddenly off. Rated Watts for HD20 are 254W(std), 305W(bright mode).
I made a complaint to APC and technician came and did below tests.
- Mains off, UPS on -> we switched on the PJ, PJ went live without any issues.
- Then we switched the mains on. After few minutes switched the mains off, both UPS and PJ went off with UPS sounding overloading alarm.
wondering how PJ switched on with mains off/UPS on (step 1) if this can be overloading issue.
Now the technician measured the voltage in these scenarios.
- Mains on/UPS on, meter reading is 235V.
- Mains off/UPS on, meter reading is 160V
I think optoma HD20 needs minimum 180V hence my UPS not able to support it. APC technician suggested to go for BR1000 or BR1100 having 1kva/1.1kva. He said both models will have minimum 200V when the power goes off (instead of 160V my current UPS has).
I need to confirm by measuring the same before going for it.
FM's(especially HD20 owners) - can you please let me know the UPS that are using and working great? My PJ is switched off without backup for about 3 times so far and I am already worried
rg,
saravanan
I have paired this model APC BR600 (360W ) costing 2.5k to my optoma HD20.
But when the power goes off, PJ also went suddenly off. Rated Watts for HD20 are 254W(std), 305W(bright mode).
I made a complaint to APC and technician came and did below tests.
- Mains off, UPS on -> we switched on the PJ, PJ went live without any issues.
- Then we switched the mains on. After few minutes switched the mains off, both UPS and PJ went off with UPS sounding overloading alarm.
wondering how PJ switched on with mains off/UPS on (step 1) if this can be overloading issue.
Now the technician measured the voltage in these scenarios.
- Mains on/UPS on, meter reading is 235V.
- Mains off/UPS on, meter reading is 160V
I think optoma HD20 needs minimum 180V hence my UPS not able to support it. APC technician suggested to go for BR1000 or BR1100 having 1kva/1.1kva. He said both models will have minimum 200V when the power goes off (instead of 160V my current UPS has).
I need to confirm by measuring the same before going for it.
FM's(especially HD20 owners) - can you please let me know the UPS that are using and working great? My PJ is switched off without backup for about 3 times so far and I am already worried

rg,
saravanan